Issues with the inlet pipeline size of the oil tank loading pump

2016-06-24View Original

Thread Content

Originally, there was a pump with a capacity of 10 m3/h; the outlet pipelines from the oil tank were all DN50 in diameter. The oil was somewhat viscous, which resulted in a long loading time. I now want to switch to a pump with a capacity of 50 m3/h, and I’d like to change the inlet pipeline to DN100. The problem is that whether we make an opening elsewhere or enlarge the existing DN50 pipe, it’s necessary to empty the tank. I don’t want to do this; instead, I want to keep the 1.5-meter-long DN50 pipe at the tank’s outlet and replace it with a DN100 pipe later. In other words, should the inlet of the loading pump be of smaller diameter first and then changed to a larger diameter? Is that possible? Will the loading speed increase? The tank liquid level is generally around 50,000–45,000 mm, and the distance from the tank outlet to the pump inlet is about 18 m. I would appreciate your advice
Reply #22016-06-24
Even after connecting 50 and 100, cleaning is still required; the pump outlet usually goes from a smaller diameter to a larger one, which can easily cause the pump to get stuck
Reply #32016-06-24
No, the oil has high viscosity and low flow rate. You can try using a pipeline pump. Try to shorten the pipeline between the tank inlet and the pump inlet
Reply #42016-06-24
What kind of pump was used originally, and what were the viscosity and temperature values?
Reply #52016-06-24
For shielded pumps, viscosity decreases as temperature drops, but it does not exceed 0.1 Pas
Reply #62016-06-24
The lower the temperature, the higher the viscosity should be, right? Positive displacement pumps offer better delivery performance, right?
Reply #72016-06-24
For this 1.5m DN50 pipeline leading from the reserved tank outlet, it is necessary to verify what the flow rate will be; a too high flow rate may pose a safety risk.
Reply #82016-06-27
{:3_64:} Add a buffer tank in front of the pump; fill the tank ahead of time before loading, then start the pump and open the valve. This method is faster than before, but it will still be slower than using a normal DN100 pipe. Adjust the valve at the pump outlet according to the actual conditions – don’t open it too wide, or else the pump will run out of fluid. Determine the appropriate opening degree based on your specific pump. . The buffer tank doesn’t need to be very large either; 1 cubic meter should be sufficient

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.