For sending a 24VDC signal to the PLC, a 1.5 square millimeter control cable is used – will there be any issues transmitting over a distance of 300 meters?

2016-08-18View Original

Thread Content

RT is located about 300 meters away from the PLC cabinet; could signal distortion occur due to this long distance?
Reply #22016-08-18
It is best to have a shielding layer. A 1.5 wire; one with a 500-length was used on site.
Reply #32016-08-18
The current signal should be fine.....
Reply #42016-08-18
Agreed. It’s best to have a shielding layer; 300 meters is a bit too far.
Reply #52016-08-20
There’s no problem at all; it’s not even necessary to connect the shielding layer. No issues at all
Reply #62016-08-20
As long as it runs along the instrument cable tray and is not laid together with power cables of 220V or higher, there is no problem; shielding is not necessary
Reply #72016-08-20
Now, both types of instrument transmitters use 4-20ma current output, so as long as the gauge can be illuminated, this distance is sufficient. It’s okay either way
Reply #82016-08-21
No problem. 800M will work just fine. As long as a suitable shielded cable is chosen. However, it’s hard to say the same for electromagnetic flowmeters; it’s best to do some calculations.
Reply #92016-08-22
1. Is it a digital signal, an analog signal, or a high-frequency pulse input signal? 2. If it is a digital voltage signal, the capacitance of the wiring will undoubtedly affect the response time of the signal. 3. For high-frequency signals, excessively long cables can have catastrophic effects :)
Reply #102016-08-22
There are no issues with DI/O. As for AI/O, as long as it is connected through the instrument tray and there is no voltage above 220V, then there are no problems:victory:

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.