Is it okay to use buried gas pipes in the substation?

2016-08-25View Original

Thread Content

Due to spatial constraints, the gas pipeline needs to pass through 35KV and 6KV distribution rooms; is it feasible to bury it? Are there any such regulations?
Reply #22016-08-25
Yes, seamless steel pipes should be buried at a sufficient depth; the welds must undergo 100% non-destructive testing. They should extend a sufficient distance on both sides, with leak detection measures in place at both ends

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.