The liquid level at the interface is measured using a differential pressure level gauge. At the lowest liquid level, the pressure difference between the positive and negative chambers of the gauge is -2796 Pa, while the gauge’s range is 5884 Pa. Therefore, when the gauge outputs a signal of 12 mA, what is the differential pressure signal received by the gauge in Pa? Please provide the calculation process, thank you
Reply #22016-10-19
The lower limit of the gauge is -2796 Pa, and its range is 5884 Pa; therefore, the upper limit of the gauge is 3088 Pa. When an output of 12 mA is achieved, this corresponds to half of the range, that is, (3088 – 2796)/2 = 146 Pa
Reply #32016-10-20
This post was last edited by jcicwht on 2016-10-20 at 10:10. It should be 146 Pa. (12-4)/(20-4)=x/5884; thus, x=2942 Pa. -2796+2942=146 Pa
Reply #42016-10-20
5884/2=2942. 2942-2796=146pa.
Reply #52016-10-20
When 12mA is output, it corresponds to half of the range, that is, 5884/2=2942Pa; The lower limit of the gauge is -2796 Pa; therefore, the differential pressure signal of 12 mA output by the gauge corresponds to 2942 – 2796 = 146 Pa
Reply #62016-10-20
When the transmitter outputs 12mA, the input differential pressure is 50%; the zero-point drift is -2796 Pa. The transmitter’s range is from -2796 to 3088 Pa. Therefore, the pressure value at 50% is = 50% * 5884 – 2796 = 146 Pa
Reply #72016-10-20
The question is not precise; when the liquid level is at its lowest, it is not necessarily the lower limit of the range.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.