I have a question for everyone: in what kind of substations is it necessary to have fire-fighting sand?

2016-11-18View Original

Thread Content

Do all power distribution rooms need to be equipped with fire-fighting sand? Are there any regulatory requirements or standards?
Reply #22016-11-18
Who knows the answer to this? I’ve never seen yellow sand in the distribution room.
Reply #32016-11-18
The key is whether there are any relevant regulatory requirements or standards!
Reply #42016-11-18
I’ve seen it before, but it was outdoors, a red bucket hanging on the wall. There aren’t any anymore; they’re all fire extinguishers now.
Reply #52016-11-21
Paragraph 3 of Article 12.4.2 of GB50074-2014 \"Code for Design of Oil Depots\" requires that the power distribution room be equipped with no less than 2 cubic meters of fire extinguishing sand

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.