Thread Content

Is there a difference between Ex d IIC and E*a IIC?
Reply #22016-12-01
Ex d IIC is dual-certified and suitable for intrinsically safe and flameproof applications, while E*a IIC is only intrinsically safe.
Reply #32016-12-01
This post was last edited by daguhualiuying on 2016-12-1 at 14:26. I don’t understand why intrinsically safe instruments still need to be explosion-proof; intrinsically safe design already serves to limit the energy of ignition sources. Or could we just use explosion-proof instruments instead? Why use both intrinsically safe and explosion-proof designs?
Reply #42016-12-01
The Ex d [ia] IIC explosion protection type is a composite type, featuring an intrinsically safe main unit along with devices connected to its intrinsic safety output. E*a IIC intrinsically safe and explosion-proof. ? ?
Reply #52016-12-01
;P What a great speech upstairs – Benan should be fine
Reply #62016-12-01
Flameproof instruments are much more expensive than intrinsically safe instruments. But some instruments can only be made in an explosion-proof design.
Reply #72016-12-02
It’s precisely because I don’t need it that I hope someone who understands can explain it to me; I don’t think this guy gave any good suggestions at all :(
Reply #82016-12-02
Intrinsic safety instruments need to be part of an intrinsic safety circuit in order to provide explosion protection, such as safety barriers and intrinsic safety cables. Explosion-proof instruments do not require these elements to meet explosion protection standards. It can be said that instruments with dual certification have a wider range of applications, which is an advantage
Reply #92016-12-02
Ex d [ia] IIC devices are flameproof instruments, but some of them meet intrinsically safe requirements. Typical application: The power supply section of the instrument is separated from the main body, or an inner casing is used within the instrument enclosure. Power supply is intrinsically safe, while the main unit is intrinsically safe. Commonly found in mass flow meters or analytical instruments of certain models ; The instrument is intrinsically safe, while the wiring section is intrinsically safe as well. Some valve positioners put the wiring in a separate box; that’s what it means.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.