How to determine if there is internal leakage in a vaporization lockhopper valve?

2016-12-28View Original

Thread Content

Reply #21970-01-01
The question is, which valve are you referring to?
Reply #31970-01-01
The lockout valve should be equipped with a transmitter for measuring pressure or differential pressure; in the event of a leak, an alarm will be triggered for either the pressure or differential pressure, and this can be seen on the display
Reply #41970-01-01
There are many types: pressure filling valves, pressure relief valves, flushing water valves, slag locking valves, and so on
Reply #51970-01-01
1. When the coal powder lockhopper valve is closed, monitor the changes in lockhopper pressure. 2. Check whether the pressure relief pipeline of the slag lock hopper is hot; check the pressure with the valve closed, and see if there is any overflow in the flushing water tank
Reply #61970-01-01
The temperature of the lockhopper: internal leakage in any of the valves can cause this temperature to rise gradually. This is usually visible on the computer, after which it is necessary to check whether the pipelines connected to those valves are hot, in order to determine which valve is leaking
Reply #71970-01-01
Specifically speaking, there are several valves here

Submit a Project

Need technical support or have a project requirement? No registration needed.

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.