For coke oven gas at 0.4 MPa in DN700 pipes, what type of valve is needed for cutting off the flow?

2019-11-27 View Original

Thread Content

I hope the experts here can help me figure this out: For a coke oven gas system with a pressure of 0.4 MPa and pipes of DN700 size, what type of valve should be used for cutting off the flow? The pressure is relatively high; is it feasible to use a combination of a butterfly valve and a blind valve?
Reply #2 2019-11-27
The pressure isn’t very high; I’m thinking of using a butterfly valve in combination with a blind valve, but I’m not sure whether the blind valve can still be used at pressures above 0.25 MPa – it seems that its maximum operating pressure is only 0.25 MPa
Reply #3 2019-11-27
Is a single butterfly valve sufficient? I’m thinking of using a combination of a butterfly valve and a blind valve, but I couldn’t find any models of blind valves suitable for pressures above 0.4 MPa
Reply #4 2019-11-27
If a blind plate is used on the butterfly valve, it should no longer be possible to open the valve. P; if a butterfly valve can be used, then the correct installation sequence should be butterfly valve + short flange pipe + blind plate/cap.
Reply #5 2019-11-28
It’s not a blind plate used on the butterfly valve, but rather a combination of a butterfly valve and a blind plate valve; however, no blind plate valve with a pressure rating of 0.4 MPa was found
Reply #6 2019-11-28
Provide the temperature parameters; a ventilation butterfly valve can achieve a leakage rate of 1%, or a triple-eccentric butterfly valve can be used. I was wondering if 700-bore ball valves are available. How much would they cost? . . . There are pictures on my homepage: high-temperature butterfly valves used in steel mills :D:D
Reply #7 2019-11-28
DN700 ball valve, what are you thinking, buddy? The butterfly valve is the preferred choice!
Reply #8 2019-11-28
At a temperature of 100°C, wouldn’t there be leakage if only one butterfly valve is used?

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.