After the interlock shutdown due to a disruption in the main air supply to the catalytic unit, when is the interlock reset?
Reply #22019-03-03
After stopping and checking the valve operation, it can be reset by removing the mandatory conditions
Reply #32019-03-03
After the main fan’s interlock mechanism is activated, the corresponding interlocks for the two reactors as well as the feeding interlock will also be activated. Before preparing to start the main fan, it is necessary to reset all these interlocks. Of course, there is a sequence to this: the main fan interlock is the highest priority, followed by those of the two reactors, and finally the feeding interlock
Reply #42019-03-06
I agree with what was said on the first floor: as long as it is confirmed that each safety valve is functioning properly, it can be reset. Since all of the steam valves involved in the interlock system are in the fully open position, you need to get ready to resume production immediately.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.