There are 3 compressors in the system, with 2 in use and 1 as a backup; the exhaust gas is directed to the same air storage tank. It is now necessary to monitor the pressure in this storage tank after the compressors discharge their gas, and if the pressure drops, the compressors should be started. The manufacturer said that 3 transmitters need to be installed at the gas cylinder location. May I ask: Is it possible to install only 1 transmitter, with the signal sent to 3 PLC cabinets? If possible, how can it be achieved? (Note: The manufacturer has provided 1 PLC control cabinet for each compressor.)
Reply #22017-02-17
Yes, it’s a price/current signal distributor that divides the signal into three parts and sends them to each PLC. The control pressure can be set; for example, if the pressure is set at 1 MPA, pressing the start button activates the first compressor. When the pressure doesn’t reach that level, the second compressor is activated, which achieves a constant pressure control effect
Reply #32017-02-17
If a voltage signal is connected in parallel to the modules of the three PLCs, and each of the three PLCs sets different start pressure conditions for the corresponding compressor, it is theoretically possible to do so. I haven’t tried it, so please correct me if I’m wrong.
Reply #42017-03-16
Personally, I think three units would be better, so as to enable separate control of the start and stop for each compressor
Reply #52017-03-27
It is best to use 3 pressure gauges to implement a two-out-of-three redundancy system for monitoring the pressure in the air storage tank at the compressor outlet; when the pressure drops, the backup unit is activated. Why not use three compressors and instead go with a single PLC for centralized control? Or the system is also redundant, wouldn’t that make the reliability even higher? !

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.