Issues with air compressor starting under reduced pressure

2017-05-21View Original

Thread Content

The total voltage is 35KV/10kv. The air compressor is an asynchronous motor with a voltage of 10kv and a power rating of 6000. I would like to know how to select a voltage reduction starting device, and what issues need to be taken into consideration?
Reply #22017-05-24
First, obtain some data from the power grid: what is the capacity of the main transformer? Are there any requirements for speed control of the air compressor? Are more requirements performance requirements or investment cost requirements? Depending on the requirements, variable-frequency starting, solid-state soft starting, water-resistance cabinet starting, or autotransformer step-down starting can all be selected. The main consideration is still the specifics of the project and the conditions of the power grid. In a previous project, in order to reduce costs, three 10kV motors were used, with autotransformer starting for a 1-to-3 drive configuration
Reply #32017-05-31
Start by boiling the resistor or using an inverter. Soft start is also an option; the direct start current is too high
Reply #42017-05-31
The total capacity of the 35KV transformer is 31.5; The air compressor does not require variable speed. Additionally, the motor power of the air compressor is 700 kW ; Can it pull two at once? ; Which blood pressure control method is better?
Reply #52017-06-09
We have 10kV, 4000kw air compressor motors; the magnetically controlled soft starters used in the past did not perform well, and various problems arose with them after several years of operation. It was later replaced with a high-voltage solid-state soft starter, and it has been operating well for the past two years. As for driving one vehicle to pull two, there’s no theoretical problem with that; driving one vehicle to pull multiple vehicles is also fine, it’s just a matter of whether you’re willing to make the investment. During startup, the soft starter operates on a short-time basis; adding a switching device enables multi-load functionality.
Reply #62017-06-14
For the reduced-voltage starting of large motors like this, water resistors are a suitable choice – they are inexpensive, do not cause harmonic currents, but require more space for installation.
Reply #72017-06-17
Our company’s 1600kw air compressors use Changsha Aoto high-voltage solid-state soft starters; they have been in use for almost 4 years now and are functioning properly.
Reply #82017-06-28
Several parameters are required for selecting the starting device of large high-voltage motors. 1. Capacity of the transformers on-site and remaining power capacity. 2. Capacity of transformers in the upstream substation and remaining power capacity. 3. Length of transmission lines and wire gauge. 4. Whether speed control is required for the motors. 5. Whether investment considerations are necessary. 6. Whether site considerations are necessary. Large-scale high-voltage power distribution requires comprehensive consideration; it’s not something that can be decided simply based on experience

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.