Summary of the situation: The environmental requirements dictate an explosion-proof classification of Zone 1. When the plant was built, the power supplies for the motors of all pumps, as well as those for the control panels on site and various instrument terminals, were connected using plastic-coated metal hoses along with explosion-proof connectors before being fed into the wiring boxes. Problem solving: Does this type of connection meet the explosion-proof requirements for Zone 1? Is it necessary to replace it with an explosion-proof hose and explosion-proof connector before connecting it to the junction box? Are there any requirements? Since the volume of work is very large, I’m seeking solutions. Thank you!
GB3836.15-2000 Electrical equipment for explosive atmospheres – Part 15: Electrical installation in hazardous locations (except coal mines). Chapters 9 and 10 specify requirements regarding cables and conduit systems in explosive areas. I hope this is helpful to you. Additionally, the existing standards do not require the use of explosion-proof hoses; it is sufficient as long as the way in which the cables are introduced does not compromise the explosion-proof rating of the equipment itself!