Problems with air compressor aerial drop tests

2017-07-11View Original

Thread Content

What is the purpose of the aerial drop test for 10KV air compressors? In what state should the high-voltage circuit breaker be to conduct tests?
Reply #22017-07-13
Check whether the control circuit is functioning properly, including opening and closing, signal lights, interlock operations, etc; The high-voltage circuit breaker trolley should be in the testing position.
Reply #32017-07-15
The switch is in the test position. Function: 1. Check whether the secondary control circuit is operating properly. 2. Is the opening and closing mechanism of the switch itself functioning properly? 3. Check whether the protection interlock is functioning properly.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.