When starting the high-voltage soft starter, why is there an abnormal differential current alarm for the main transformer on the corresponding side?
Reply #22018-06-08
When a high-voltage soft starter starts up, high-order harmonics are generated. Due to the differences in the volt-ampere characteristics of the protection windings of the current transformers on the high-voltage and low-voltage sides of the main transformer, it is normal for a differential current overload alarm to occur; this will not cause the differential protection of the main transformer to trip. If there are concerns, the main transformer differential current over-limit alarm setting can be modified.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.