【Daily Question】Utilities - HVAC - 20200107

2020-01-07View Original

Thread Content

Regarding the exhaust outlets for accident ventilation, which of the following does not comply with the regulations? A. It should not be installed in areas where people frequently stay or walk through. B. The exhaust outlets must not face areas under aerodynamic shadowing or in regions with positive pressure. C. When the exhaust gas contains flammable gases, the distance between the exhaust outlet of the emergency ventilation system and any locations where sparks might fall should be greater than 10 m. D. The horizontal distance between the exhaust outlet and the air inlet of the mechanical ventilation system should be at least 20 m. Answer: C
Reply #22020-01-07
C. When the exhaust gas contains flammable gases, the outlet of the emergency ventilation system should be more than 10 m away from any location where sparks might fall

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.