Is it necessary to use a disconnecting clip for the grounding of street lights in chemical plants?

2021-10-08View Original

Thread Content

As the title suggests: Is it necessary to use a disconnecting clip for the grounding of street lights in chemical plants? Is there any specific standard support available? Please let me know if you are aware of it. Thank you!
Reply #22021-10-08
It is necessary; it relates to the requirements for lightning protection grounding. By installing a disconnecting clip and then disconnecting that clip during testing, it is possible to accurately measure the grounding resistance. Specifically, refer to GB50343 and GB50057.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.