HCBBS Forum (English)
Submit Chemical Projects / Find Solutions
Amplify Your Requirements on a Broader Chemical Platform *Engineering · Technology · Equipment · Solutions*
Submit Request

Pipeline diameter issues at LNG vaporization stations

2018-11-22View Original

Thread Content

I wonder what determines the diameter of the inlet and outlet pipelines at LNG vaporization stations? For example, the station has 8 150m3 storage tanks, 4 LNG unloading platforms, and 10 4000m3/h air-cooled vaporizers; what should be the appropriate diameter for the LNG inlet and outlet pipes in such a station?
Reply #22018-12-04
The LNG flow rate is calculated based on a flow velocity of less than 1 m/s
Reply #32018-12-06
This flow rate is too low; it should generally be above 4 meters:lol
Reply #42018-12-14
The standard is no more than 7 m/s; 3 m/s is generally sufficient
Reply #52018-12-19
(1) Generally, the LNG flow velocity is set at 2-5 m/s; the pipe diameter should be a round number, and then the flow velocity can be calculated inversely – anything close to that value will suffice; (2) 150 storage tank, general liquid outlet DN50 or DN65 ; (3) The gasification station above is equipped with 10 4000-type air-temperature gasifiers, arranged in 2 groups; each group has a gasification capacity of 20,000 Nm3/h. An 80-sized pipeline is sufficient for the liquid phase, while a 50-sized pipeline is required at the inlet of the gasifiers.
Reply #62018-12-23
Does the piping in the LNG tank farm need to be insulated? Thank you!
Reply #72019-01-02
The liquid phase definitely requires insulation, as well as inlet and outlet pipes for the liquid.
Reply #82019-01-03
Based on the capacity of the vaporizer, it is estimated that the gas consumption will be over 20,000. To maintain a stable supply, there needs to be a balance between inflow and outflow; accordingly, the inflow and outflow of liquid should be 34 cubic meters, with the liquid-phase pipeline needing to have a capacity of at least 80 cubic meters.
Reply #92019-07-02
Hello, may I ask on which company’s data this calculation is based? Could you provide the formula or an explanation of how the calculation was done? Thank you very much

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.