What could be the reason for high suction pressure and low superheat in a refrigeration compressor?

2017-04-07View Original

Thread Content

The suction pressure of the screw refrigeration compressor is high, the slider load is 42%, and the superheat is only 0.4°C; it is not possible to increase the load any further. What could be the reason for this?
Reply #22017-04-07
Is the exhaust pressure normal? If the exhaust pressure is low while the inlet pressure is high, it’s likely that the throttle valve is damaged. If both the exhaust pressure and the suction pressure are high, it is likely that there is too much refrigerant.
Reply #32017-04-07
The exhaust pressure is normal, slightly lower than before; the liquid levels in the condenser and economizer are both normal
Reply #42017-04-07
When you say the throttle valve is broken, are you referring to the poor throttling effect and the large amount of fluid flowing in?
Reply #52017-04-09
Mm-hmm, you said the temperature rise is only 0.4, and the inlet pressure is a bit high; I think there’s some excess cold energy accumulating. If nothing else is wrong, it’s likely that the flow rate has increased, so I suggest you check the throttle valve.
Reply #62021-07-16
1. Consider whether the refrigerant is carrying liquid, 2. Check the evaporator liquid level; 3. Check the flow rate and temperature of the hot material.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.