What causes the shutdown of a screw chiller due to a low suction pressure alarm?

2017-12-28View Original

Thread Content

The filter on the connection pipeline from the evaporator to the machine head is frozen – has water gotten in?
Reply #22018-01-01
This post was last edited by tie008 on 2018-1-1 10:37: \"Filter freezing in the pipeline connecting the evaporator to the machine head\" – The evaporator might be leaking~~~ If it’s the condenser that’s leaking, then the evaporator is blocked~~~
Reply #32018-01-02
Evaporator leak: water from the shell side enters the Freon circuit; If the oil has been changed with fluorine-added fluid, the newly added Freon contains water, and the newly added lubricant is of poor quality ; The frozen pipes/filters need to be cleaned, and the entire system should be dehydrated using silicone… It’s also necessary to consider whether there might be issues with the insulation of the compressor motor……
Reply #42018-03-01
Thank you all; I checked and found a leak in the copper tubes of the evaporator. It’s already blocked; change the oil and refrigerant.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.