The inlet valve of the centrifuge is set at 100%, and the bypass valve is still open. I would like to ask for advice from those with more experience

2019-06-23View Original

Thread Content

The centrifuge’s intake valve is set at 100%, the bypass valve remains open, and it still shows a minimum load – is this normal? What could be the reason?
Reply #22019-06-24
First, the unit needs to be maintained; Second, it is confirmed that the gas consumption at the backend is low; the unit is unable to adjust the minimum gas flow rate and can only vent a small amount of gas.
Reply #32019-06-24
Hello, the cooler has just been cleaned and the air filter has been replaced with a new one. If the air consumption at the rear end is low, the opening degree of the intake valve should decrease; it shouldn’t be 100%. The same is true for the other two units – their intake valve opening degrees are at 100% while the bypass valves are almost closed. When air consumption is low, the opening degree of the intake valve decreases
Reply #42019-07-04
An exhaust valve opening of 0-21% essentially means complete evacuation; it might be due to excessive pressure in the main pipeline, causing the air compressor to adjust automatically. Is there any equipment under maintenance at the end of the pipeline?
Reply #52019-09-29
Logically, the intake valve should be 100% open while the bypass valve should be closed. Is it connected to pipes shared with other units, resulting in a low total flow rate that prevents the unit from operating at full capacity?

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.