[Discussion Thread 14] Can NPT thread connections be used for the ports of a 13 m3 liquefied petroleum gas storage tank?

2019-02-17View Original

Thread Content

bg14.jpg【Discussion Thread 14】Can an NPT thread connection be used for the piping of a 13 m3 liquefied petroleum gas storage tank? Answer to the question: Incorrect, but no specific and valid source was provided, so doubts remain. I hope the experts will actively participate in the discussion: handshake
Reply #22019-02-17
Basic provisions for the structure of LPG pressure vessels in code of regulations, Article 37-----Flange connections
Reply #32019-02-18
Is this a requirement specified in the 1999 version of the regulations?
Reply #42019-02-18
According to clause 3.2.5 of the standards, this clause appears to specify the requirements for using pipe flanges; however, item (2) of this clause does not state that threaded connections are not allowed. Please look for the relevant basis again.
Reply #52019-02-18
Gauge instruments and thermometers use threaded connections. How else should it be set?
Reply #62019-02-18
You can take a look at TSG-2016 P22 3.2.5 (2)!
Reply #72019-02-18
The 1999 version of the regulatory standards states that when designing storage containers for liquefied petroleum gas, it is necessary to follow the provisions of the industry standards HG20592–20635, and select pipe flanges, gaskets, and fasteners with a pressure rating higher than the design pressure. For the first dust seal surface connected using flanges, a high-neck butt weld flange, a metal wound gasket (with an outer ring), and high-strength bolts should be used together.
Reply #82019-02-18
As I understand it, this clause specifies the requirements when using pipe flanges; it does not mandate that such equipment must be connected using flanges only, excluding threaded connections.
Reply #92019-02-18
The older version stated this point quite clearly. The new version, taking into account the role of the regulatory standards, has removed many specific requirements; however, this is simply due to the standard’s nature, and it doesn’t mean that those requirements are incorrect or inappropriate in any way
Reply #102019-02-19
No matter which version, it’s not apparent that threaded connection cannot be used.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.