Discussion on the fire separation distance for emergency ponds in chemical engineering construction projects

2024-08-29View Original

Thread Content

Article 6.6.3 of the \"Environmental Protection Design Standards for Chemical Engineering Construction Projects\" GBT 50483–2019: When accident wastewater contains substances of Category A, Category B, or Category C, the fire classification shall be determined as Category C; however, in emergency situations, it shall be managed as if it were of Category A; Article 4.2.8 of the \"Code for Fire Protection Design of Petrochemical Enterprises (2018 Edition)\” GB50160-2008: 4.2.8A Accident water tanks and rainwater monitoring tanks should be located in the lower areas at the edge of the plant site; they can also be arranged together with the sewage treatment facilities. The fire protection distance between the accident tank and open flames should be no less than 25 m, and the fire protection distance from elevated flares that may carry flammable liquids should be no less than 60 m. Explanation of the provisions: The accident tank is primarily used to collect contaminated fire-fighting water under fire conditions, polluted rainwater, and any combustible substances that may leak. Accident water and rainwater generally flow by gravity through pipelines to the accident water tank and the rainwater monitoring tank; therefore, these tanks should be located at lower positions on the edge of the plant area. Accident water and rainwater that fails monitoring tests must be treated to meet standards before being discharged from the plant; locating the treatment facilities together with the sewage treatment plant can reduce pipeline lengths and save energy. Since a fire accident may be accompanied by a leak of flammable liquids, fire separation distances have been specified between the accident tank, open flames, and elevated flares that may carry flammable liquids. Since the accident pool remains empty for long periods of time, no fire separation distance is required from other facilities. GB51283 does not specify clear requirements regarding the fire separation distances for accident ponds. If GB51283 is to be followed, should the fire separation distances be determined based on those for Class C open-type facilities, or for wastewater treatment facilities that contain flammable liquids? Or are no such requirements specified?
Reply #22024-08-29
In accordance with the \"Environmental Protection Design Standards for Chemical Engineering Construction Projects\" and the \"Fire Protection Design Standards for Petrochemical Enterprises (2018 Edition)\\", a fire safety distance should be considered for accident ponds. The accident tank shall be at a minimum fire separation distance of 25 meters from areas with open flames, and at a fire separation distance of no less than 60 meters from elevated flares that may carry flammable liquids. If referring to the GB51283 standard, it is necessary to conduct a specific analysis of the details and environment related to the accident tank before deciding which category of fire separation requirements should be applied. .

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.