3.8 MPa, 450°C superheated steam hydrostatic test pressure

2017-04-17View Original

Thread Content

The superheated steam conditions are 3.8 MPa and 450 degrees Celsius; the design pressure has been set at 4.2 MPa. The material 15CrMoG is chosen, with a grade of PN63. However, calculations show that the hydrostatic test pressure would need to be 9.3 MPa, which is far above the specified material grade. I would like to know how the hydrostatic test pressure should be determined.
Reply #22017-04-18
In my opinion, it is acceptable to calculate the hydrostatic test pressure at 9.3 MPa; however, it is also necessary to ensure that the circumferential pressure of the components under test conditions does not exceed the specified value, otherwise the test pressure needs to be reduced.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.