Regarding the issue of fire separation distances

2017-08-14View Original

Thread Content

Seeking advice: In Table 4.3.1 of the \"GB50016-2014 Code for Fire Protection Design of Buildings\", regarding wet combustible gas storage tanks (total volume V, in m3), for example, what is the fire protection distance required between 2 wet combustible gas storage tanks with a volume of 5000 m3 each and a pile of combustible materials? Should the fire protection distance be calculated based on the volume of one tank or based on the total volume of both tanks? I’m a bit confused and would appreciate guidance from those with experience.
Reply #22017-08-14
Both storage tanks must meet the requirements.
Reply #32017-08-14
Table 4.3.1 of GB50016 specifies in the first row the wet-type flammable gas storage tanks (total volume V, in m3)

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.