Is it possible to install a check valve?

2017-12-31View Original

Thread Content

The low-pressure centrifugal fan used in my system is designed to operate at a pressure of no more than 0.07 MPa. When the fan malfunctions, the medium often flows back due to the valves not closing properly. For safety reasons, I want to install a check valve at the fan’s outlet; I’m not sure if this will work. Given the low pressure generated by the fan, I wonder whether it will be able to push aside the check valve. Please share your thoughts; thanks, bonus points for helpful answers
Reply #22017-12-31
A check valve with reduced pressure should work.
Reply #32018-01-01
I already replied in another thread yesterday~~~
Reply #42018-01-02
A one-way valve can’t guarantee a tight seal, right? It is recommended that you install a shut-off valve linked to the fan via interlock. The fan is faulty, and the shut-off valve closes immediately.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.