I have a question: why does the steam control valve on the steam heating pipeline keep adjusting either resulting in over-temperature or insufficient adjustment?

2018-10-11View Original

Thread Content

I have a question: why does the steam control valve on the steam heating pipeline keep adjusting either resulting in over-temperature or insufficient adjustment? Is there any way? ? Is the temperature control stable under your operating conditions? Thank you
Reply #22018-10-11
Temperature conditions inherently have a lag, and they can be adjusted by correlating them with flow rate or pressure
Reply #32018-10-11
Do you mean cascade control? ?
Reply #42018-10-12
There is a temperature lag, and in addition, the PID parameters of your control valve are not set properly
Reply #52018-10-12
There are two possible reasons for the situation you described: one is the adjustment method, and the other is the type of control valve as well as its diameter. The diameter should be selected based on the amount of steam required under stable heating conditions. Meets the required adjustment accuracy.
Reply #62018-10-13
If the air supply is unstable, an energy storage tank can be added
Reply #72018-10-13
First, adjust the PID parameters; if that doesn’t work, try modifying the valve flow rate
Reply #82018-10-16
To sum it up, it’s already very detailed. The steam pressure should not fluctuate significantly; a proper PID setting, along with restrictions on the steam valve position, is necessary. If the load requirement is not met, replace the reboiler. Provide a reasonable value for the condensate pressure.
Reply #92018-10-16
Firstly, it is necessary to ensure that there is no condensed water in the steam pipeline system; water removal procedures should be strengthened. Secondly, the steam pressure in the pipeline system must be kept stable. Additionally, it is important to check whether the PID control parameters are appropriate; if not, manual adjustment may be required

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.