Dear experts, I would like to ask whether compressed air and nitrogen storage tanks are necessary. Some people say that without them, an air supply cannot be guaranteed in the event of a power outage, which poses a safety risk. If such tanks are needed, how should their capacity be determined? Should they be placed before or after the control valve? Please give me some advice!
The capacity of the gas storage tank can be calculated in accordance with chemical industry standards; it is recommended that it be placed before the control valve.
I have a question regarding process issues: is there any direct relationship between the volume of the storage tank, as well as the size of its inlets and outlets, and factors such as flow rate and pressure?
It is definitely necessary in actual production; not only for safety reasons – without storage tanks, there will be pressure fluctuations! , especially nitrogen
It’s not just a safety hazard; in the presence of air lock, the control valve cannot return to its safe setting. The discharge volume of the device’s safety valve **exceeds the design value, causing overpressure in the equipment.** :lol:@
Refer to standard HG/T20510; this standard can be downloaded online
4.4 Determination of the volume of the gas storage tank 4.4.1 The gas supply system should be equipped with a gas storage tank of sufficient capacity. The volume of this tank shall be calculated using the following formula: V = 60*qV1* t*ρ0/(ρ1-p2). Where: V – volume of the storage tank, in m3; qV1 – designed gas supply capacity of the gas supply system, in Nm/h; p1 – normal operating pressure, in kPa; ρ2 – minimum pressure at which gas is delivered, in kPa; p0 – atmospheric pressure, usually p0 = 101.33 kPa; t – holding time, in minutes; unless otherwise specified, this value can range from 15 to 20 minutes.
Considering the company’s situation, we’ll use one 10m3 unit each, to be placed in front of the pressure relief valve