What is the fire hazard category of the air compressor station? What are the corresponding standard specifications for reference?
Reply #22019-02-27
Category B, same as oxygen stations, air separation plant buildings
Reply #32019-02-27
Oil-lubricated air compressor stations are classified as Class D; Oil-free lubrication (air free of oil) is classified as Category V~~
Reply #42019-02-27
Personally, I think what was said on the fifth floor makes sense; the appendix mentions an air separation station, not an air compression station
Reply #52019-02-28
If the air separation plant only produces nitrogen and oxygen is released into the atmosphere, does this plant still need to be classified as a Class B fire hazard?
Reply #62019-08-09
GB50029-2014 Oil-free Class V, Oil-containing Class D
Reply #72019-08-10
In accordance with GB50029-2014 \"Code for Design of Compressed Air Stations\"

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.