What is the function of the pipe between the inlet pipe and the outlet pipe? Why is this pipe needed? T1107 is a heat exchanger; I’m not sure what the purpose of this pipe installed between the cooling inlet water and the cooling return water is Is it necessary to add it? Newbie seeking advice
Reply #22019-11-13
Close the valves during heat exchanger maintenance.
Reply #32019-11-13
Setting up this bypass process also serves a temperature regulation function.
Reply #42019-11-13
When it’s cold, if the equipment stops operating, this is the anti-freezing line!
Reply #52019-11-13
Thanks for the advice; it is indeed possible
Reply #62019-11-13
The only purpose of this line is to open this valve when the cooler is shut down, thereby maintaining flow in the pipeline and providing anti-freezing protection. The temperature can be adjusted by controlling the amount of water entering the cooler through the main inlet valve; using this valve for adjustment is a waste.
Reply #72019-11-13
It is not possible to determine the diameter of the bypass pipe from this diagram. If it is 50, just like the main pipeline, then this valve should be a long-stroke valve designed for preventing freezing in winter. It is likely that the circulation water pipes in your cooler are quite long, which is why a separate anti-freezing valve is needed
Reply #82019-11-14
Bypass pipeline, with anti-freezing and water circulation functions.
Reply #92019-11-14
In the north, when it’s cold and the heat exchanger is not in use, this wire is used to keep the water flowing continuously so as to prevent it from freezing; in the south, such a wire is generally not necessary
Reply #102019-11-14
This auxiliary line is essential. It’s not just for freezing protection. Circulating water needs to be circulated during short-term shutdowns or equipment maintenance.
Reply #112019-11-14
In areas in the south where the temperature remains above zero all year round, there’s no need for this, right? Even if the equipment is to be shut down temporarily, it’s sufficient to close the inlet and outlet valves of the circulating water. Moreover, if the entire system is shut down, then the circulating water will stop flowing anyway. Even during normal operation, if just one or two water coolers are to be turned off, closing the inlet and outlet valves of those coolers and stopping the circulation of water in them will have no adverse effect on the equipment or the circulating water system

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.