As shown in the diagram, why are the low pressure in the lubricating oil main pipe and the low pressure in the turbine control oil considered a logical AND condition – i.e., an alarm is triggered only when both pressures are low? Shouldn’t an alarm be issued first at 0.65 MPa?
Reply #22019-12-09
AN means general alarm.
Reply #32019-12-09
The backup oil pump will start automatically at 0.65, and there is an alarm indication on the diagram for the automatic start of the backup pump; therefore, it is acceptable that the first AND gate triggers an alarm at 0.15. But it seems a bit redundant, you know.
Reply #42019-12-15
The automatic start function is not set for controlling oil pressure; it is planned to add this feature

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.