Is it necessary to install toxic gas alarms and related equipment for sulfur dioxide?

2020-12-09View Original

Thread Content

Sulfur dioxide is classified as a toxic gas of category 2.3; is it necessary to install toxic gas alarms and related facilities? Appendix B of the standard GB50493 does not mention sulfur dioxide; is it only highly toxic gases that require the installation of gas alarm systems? GB50493 lists only some substances; what should be done regarding those that are not listed?
Reply #22020-12-09
GB50493_2019 3.0.1: When the concentration of toxic gases in the leaking gas may reach the alarm set value, a toxic gas detector should be installed
Reply #32020-12-11
It’s definitely necessary; it’s not listed in the appendix, so it needs to be set according to the requirements in the main text.
Reply #42021-01-06
It is required; Appendix B of GB/T50493-2019 specifies that it must be installed

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.