For a 220kw, 380v motor located approximately 600 meters away from the power distribution room, what gauge of cable is suitable?

2022-01-13View Original

Thread Content

What size circuit breaker and cable are appropriate?
Reply #22022-01-14
Why not use 660 volts or 1140 volts for 220 kilowatts? The cable will be much smaller this way! If 380 must be used, a 4-core copper cable with PVC insulation requires a 300 mm2 cable and an 800A switch ; For your reference only!
Reply #32022-01-14
Our distribution room only has 380v
Reply #42022-01-16
It is recommended to use 1 10kV high-voltage cable.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.