What are the requirements for the distance between the crane position and the pump?

2023-01-29View Original

Thread Content

According to paragraph 4 of clause 6.4.2 of the petrochemical regulations, the fire separation distance between the loading/unloading crane positions and the centrally located pumps should be no less than 8 meters. In the design drawings for the facility, the two pumps are placed on the unloading impact pads, and the distance between them and the crane pipes meets the 8-meter requirement. However, after checking, it turns out that the term \"crane position\" refers to the parking space, meaning the distance from those positions to the pumps is quite small. I’m not sure what’s going on here
Reply #22023-01-29
Refer to Appendix A of the petrochemical regulations regarding the starting and ending points of fire separation distances: the centerline of the crane position and the crane pipe vertical shaft

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.