What are the hazards of not draining condensate from steam pipes? Will it cause water hammer? Can water hammer in steam pipes cause serious accidents? Has anyone experienced a severe water hammer incident firsthand? Our steam pipes basically have no drain points, and we often hear loud thudding noises and vibrations coming from the steam pipes throughout the workshop; it’s really scary. Will something bad happen?
Reply #22023-08-03
Failure to drain water from steam pipes can lead to the following hazards: 1. Tiny water droplets contained in the steam flow along with it, gradually accumulating in the pipes and forming scale, which causes pipe corrosion. 2. Water rust that accumulates over time can clog pipes, affecting steam flow and the proper operation of the system. 3. In pipes without hydrophobic devices, the interface between steam and water keeps changing, generating shock waves that are transmitted to the pipe walls, increasing the stress on the pipes and causing vibration and noise. Failure to drain steam pipes at the appropriate time can also cause water hammer. Water hammer is a fluid shock wave caused by water in steam accumulating in the pipes and being suddenly forced to stop due to the rapid closing of valves or shutdown of the system. The water hammer phenomenon can cause serious accidents such as pipe ruptures and valve damage, posing significant risks to both human safety and equipment integrity. Major water hammer incidents are relatively rare, but if the steam system is not properly designed and maintained, water hammer can still cause accidents. For someone who has not experienced a serious water hammer incident firsthand, I recommend that you contact a professional steam system maintenance and safety inspection agency as soon as possible to ensure the proper functioning of the pipes and avoid potential dangers. Regarding the loud knocking sounds and vibrations in the steam pipes in the workshop you described, it seems plausible, based on intuition, that there could be a risk of water hammer phenomenon. In such cases, it is necessary to take timely action to inspect and repair pipeline issues in order to ensure the safety and proper operation of the system. .
Reply #32023-08-03
1. During the long-distance transmission of steam through pipes, if condensate accumulates and a two-phase flow is formed, it can cause shock vibrations in the pipes. If the flow is obstructed and a water plug forms, extremely high pressures can be generated, leading to damage to the pipes and equipment; 2. The superheated steam pipeline does not require a steam trap assembly; manual drainage is carried out using gate valves during startup.
Reply #42023-08-05
Problems may not be severe over short distances, but long-distance pipelines must be hydrophobic. Steam moisture content affects steam efficiency ; Water accumulation in pipes can easily cause water hammer, which impacts the pipes and leads to cracks in their welds.
Reply #52023-08-08
The \"Power Piping Design Manual\" outlines the principles and requirements for the installation of steam traps. On saturated steam pipes, steam traps should be installed at regular intervals as well as at lower positions. (There are also standards for specific settings and installation; they can be found on the forum – the original poster can search for them.) For superheated steam pipes, it is also necessary to install steam traps, which should be opened briefly when steam is supplied and closed once no water is left. Water hammer and foaming in steam pipes must be avoided! ! Severe accidents that can easily cause the pipes to crack or the pipe supports to become misaligned. This occurs especially easily during load changes and when steam supply is restored. I have encountered accidents where the steam flange gasket was pulled apart and the sliding support was removed.
Reply #62023-09-07
Non-hydrophobicity poses serious risks; in mild cases, it causes phenomena such as water hammer and vibration in pipes and equipment, while in severe cases it leads to damage to those pipes and equipment. If someone happens to be operating the valves at that time, the valve stem may be pushed out, resulting in injury to the person. I encountered such a valve accident once when I was working; fortunately, the person was using the correct technique when operating the valve, so no one was injured. Note: 1. Before introducing steam to the pipes and equipment, the drain valves should be opened first. Preheat the pipes and equipment without opening the steam valves; based on the temperatures of the drain water and the pipes, close the water supply valve finally, and then slowly open the steam valve. If water hammer sounds or vibrations in the pipes and equipment occur during this process, continue with the water supply operation following the original procedure. 2. During the normal operation of pipelines and equipment, automatic drain valves should be installed at the ends and lower parts of the pipelines. Note that when installing a steam trap, the back pressure generated by the trap should be reduced or eliminated.
Reply #72023-09-11
If steam pipes are not made hydrophobic, water hammer will inevitably occur; it’s only a matter of time – it will happen sooner or later. In severe cases, the pipes can be broken by water hammer forces. The standard specifications, namely the \"Design Manual for the Installation of Process Piping – Design and Calculation, 5th Edition\" and \"National Standards for the Design and Engineering Application of Pressure Piping, 3rd Edition\", contain tragic examples. If your steam pipes basically have no traps, you should shut down the system as soon as possible and add low-point traps. Otherwise, accidents such as heavy casualties are likely to occur sooner or later.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.