Affected by the operating conditions of production, if the flow measurement range of the orifice plate is expanded (beyond the calibrated range), will this affect the measurement and settlement?
Reply #22017-03-09
I don’t understand what you mean. If it’s beyond the range, just expand the range – the transmitter’s measurement capabilities will suffice, and since there’s no flow restriction on the target plate, the process flow requirements can be met; so it’s possible to make the necessary modifications.
Reply #32017-03-09
What was said upstairs is correct; if the orifice plate is changed, the transmitter’s range must also be adjusted.
Reply #42017-03-09
If the measurement range is expanded beyond the calibrated range of the flow meter, will it affect trade settlements?
Reply #52017-03-09
I know that. What I mean is whether it exceeds the measurement range and thus falls outside the specifications for accurate measurement
Reply #62017-03-09
There’s no problem; as long as the differential pressure value of the orifice plate is accurate, the measurement data will also be accurate after the range is expanded.
Reply #72017-03-09
However, for trade settlements, the use of orifice plate flow meters requires approval from both parties; in general trade transactions, mass flow meters or truck scales, rail scales, and similar devices are used.
Reply #82017-03-09
The steam should be transported through pipes, right? Both parties should have metering orifice plates; after the expansion is completed, both sides can carry out calculations to determine the relevant values. For flow meters in such operating conditions, two sets – one larger and one smaller – are generally provided for use in trade settlements, with the flow meter being switched depending on the supply and demand of both parties.
Reply #92017-03-09
For example, if a flow meter has a maximum measurement range of 1000 Nm3/h, will there be any errors in measurements if this value is changed to 1500 Nm3/h?
Reply #102017-03-09
We use Emerson’s vortex flow meters for the settlement of our steam trade transactions. . Kong Plate doesn’t acknowledge Fangye at all; we’re just an internal branch of the company, and yet the requirements are so strict.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.