During operation of electric control valves, when the valve position is below 14%, significant fluctuations in the valve position occur. What is the reason for this?
Reply #22017-04-21
Check whether the valve positioner and the purge air filter are clogged, which may cause the zero point to shift
Reply #32017-04-21
I couldn’t see clearly from the second floor that it was electric! This thing isn’t easy to handle; contact the manufacturer!
Reply #42017-04-21
What valve? Is it used with steam or compressed gas? The selection issue is highly likely.
Reply #52017-04-21
Personally, I think it’s the large pressure difference before and after the valve that causes vibration at low opening degrees; you might try closing the shut-off valve in front of the control valve a bit.
Reply #62017-04-21
Please answer: what are the values for medium, temperature, and pressure respectively?
Reply #72017-04-21
The valve is too large; adjust the PID.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.