I have never worked with the configuration of the JX300X central controller; now I need to create two purely manual controllers (without any measurement values). The input for Circuit 1 in the circuit settings should be connected to the output of those manual controllers, but the compilation process shows an error – I’m not sure which parameter to use. I would be extremely grateful if anyone who has used the JX300X central control system could take a look at it!
Input for Circuit 1 only supports those AI points indicated by the question mark; simply select an unused point and enter it.
This post was last edited by chensf123 on 2018-1-19 at 14:35. Thank you to the person who replied above – the problem has been resolved. It is only possible to select or enter an analog input signal; therefore, an alternative analog point was used for connection. I would like to ask again: how should the flowchart for the pop-up control panel in routine control be configured, and what should the file extension be? (For example, the pop-up panel in my manual control system.)
The issue has been resolved; the MV value of the dynamically linked data corresponds to the control module of a single circuit in the operator unit. For example, in my case, it’s the dynamic data for FV1207.MV – by clicking on this dynamic data, the control panel of the operator unit will be displayed.