There are two electric doors at the site. When operated locally, they open or close, then stop after a few seconds; attempting to operate them again also results in them stopping after a few seconds. I’m not understanding this – please provide some guidance.
There might be a problem with the setting, or there could be a mechanical failure
Has the valve developed problems such as sticking, which has resulted in excessive torque on the motor shaft and triggered the electrical thermal protection or overcurrent protection?~~
The on-site momentary operation shown on your LED screen – go to the system menu and check if there is an option similar to hold. If it’s not this issue, try increasing the torque. With limited capabilities, I can only think of these two possible reasons.
A thorough inspection is still needed, checking everything mechanical and electrical one by one. There is also a little on-site inspection. Good luck.
It’s hard to say; it will have to be checked to find out. It could be either mechanical or electrical.
Check the manual for the electric actuator and analyze it in comparison with the actual menu settings
The intelligent electric valve will display the cause of the fault; check it. Note that in the event of a power outage for the intelligent electric valve (Rotork), if the battery is depleted, the existing configuration will be lost and reconfiguration will be required. But from your description, it seems to be the motor’s overheat protection.
Well, from a simple perspective, could it be that this electric head is the type that snaps back automatically once it’s turned on, and needs to be held down by hand to remain in the on position? :lol