Methods for dealing with clogged pressure tapping pipes in instruments

2017-06-10View Original

Thread Content

I have a flow transmitter installed to measure the flow rate of raw coal gas, and it needs to be drained almost every day; otherwise it gets clogged. In such a situation, apart from shortening the pressure lead pipe (which is not possible under the current conditions), what other good solutions are there?
Reply #22017-06-10
It is recommended to find an opportunity to replace it with a wedge flow meter or a non-contact type. At this point, could we consider adding a pipeline that can periodically blow nitrogen back?
Reply #32017-06-10
By adding a pressure guide tube and a flushing tube for regular flushing, blockages can be avoided.
Reply #42017-06-11
Can’t we add more isolation fluid tanks? Or add a flushing ring
Reply #52017-06-11
This is due to an improper selection of the flow meter; the transmitter used with this flow meter is the type equipped with a capillary, which prevents clogging. You can’t change the gauge; add a purge to improve things. . .
Reply #62017-06-18
Regarding the issue of blockage, it is necessary to analyze it based on specific operating conditions. It is difficult to make an accurate judgment due to the limited information you have provided. It is therefore difficult to give reasonable advice. Only by identifying the cause can a viable solution be found. Provide the necessary information: medium properties (temperature, pressure, gas phase or liquid phase, presence of impurities), instrument installation details: length of the pressure transfer tube, whether the instrument is installed higher or lower than the pressure sampling point, etc. If the instrument is installed below the pressure tapping point, considering the use of a tank to contain the isolation fluid is an option. We use this solution for many traffic jam problems here.
Reply #72017-06-18
For more information, please send an email to yhkj_zym@sina.com along with the detailed technical specifications to see if they can be met.
Reply #82017-06-19
Could we add a filter to it for export, and replace the filter regularly? However, this won’t solve the problem completely either; let’s use a different flow meter instead
Reply #92017-06-20
The medium is prone to clogging; an isolation tank needs to be added

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.