Communication issues with Zhejiang Zhongkong

2017-09-03View Original

Thread Content

Recently, I encountered a problem: a UPS failure resulted in the loss of power to one circuit; switch A lost power, while the indicator lights on switch B were normal. However, all the data on the DCS operation station showed question marks, and communication was interrupted. The power to switch A was restored, and the data at the control station became normal again. Then I unplugged the network cable coming from switch A, and the data flow remained normal, which was strange – why was there no data when switch B was operating on its own? ?
Reply #22017-09-03
Try it again when production stops. If that doesn’t work, you can call Zhejiang University’s central control service hotline for assistance.
Reply #32017-09-06
First, it is necessary to clarify which system it is: jx300 or ECS700? It is necessary to thoroughly uncover the truth behind this matter; otherwise, it will pose a serious risk when driving in the future as well. Suggested search directions: 1. Power supply. Normal switch indicator lights do not necessarily mean that the network functions are working properly. 2. Check whether the network cables connected to the switch are plugged in incorrectly. That is, some B-network cables are plugged into switch A. Hope this helps!
Reply #42017-09-06
Are you sure you’ve understood the A and B on the controller as well as the AB on the switch? It’s really strange; I guess only by being on site can one know the exact situation
Reply #52017-09-06
Ping the address of the main control card from the operation station to check; ping all the main control cards that serve as redundancy. Check the power supply again – ensure that the redundant 24V DC power supplies are powered by two separate 220VAC sources.
Reply #62017-09-06
First, regarding the system model: it’s useless to unplug the network cable, as the two switches can still communicate as long as they have power supply; it’s better to try unplugging the power supply of switch A

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.