Two signal-controlled control valves

2017-09-04View Original

Thread Content

Can two signals be used to control one control valve? Adjust the discharge control valve of the reaction vessel according to temperature, and automatically close it during feeding. DCS system
Reply #22017-09-04
Yes, temperature and flow rate can be used to form a cascade control system.
Reply #32017-09-04
Use a temperature control valve, and interlock the closing of the valve with the feed signal.
Reply #42017-09-04
Select control. Programming implementation of DCS system.
Reply #52017-09-04
It can be achieved by setting up an interlock in the DCS. When the feed flow rate > 0, this control valve MV = 0. Alternatively, you can add a solenoid valve to the control valve’s air line to directly interlock and cut off the flow. That’s what the original poster meant, right?
Reply #62017-09-04
One control signal, one switch signal
Reply #72017-09-05
Sure, create a program to interlock the two valves
Reply #82017-09-05
Common cascade control and multi-loop logic control can meet the requirements.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.