2017-09-04View Original

Thread Content

There is an electromagnetic flow meter with a DN450 rating in the plant. Water is pumped into the 450-sized pipeline through 5 identical pumps via 100-mm diameter pipes. The flow meter is located about 6 meters away from the nearest pump; one end of the pipeline is sealed, and the outlet end of the pipeline is raised to ensure proper storage. The capacity of each pump is 100 cubic meters. Flow occurs when one pump is in operation, but why is there no flow when two pumps are used?
Reply #22017-09-04
The signal of the electromagnetic flowmeter is in the millivolt range; first, check whether the grounding of the electromagnetic flowmeter is proper.
Reply #32017-09-04
What does it mean that the other end of the pipe is sealed?
Reply #42017-09-04
It would be best to have a piping diagram, as it makes analysis easier
Reply #52017-09-04
Won’t there be any flow even if 2 water pumps are turned on arbitrarily? Is it okay to run 3 units?
Reply #62017-09-04
Modern electromagnetic flowmeters generally use alternating magnetic fields, which allow them to effectively avoid interference from external static electromagnetic fields even in the absence of grounding; therefore, any lack of readings is likely not related to interference. If possible, the original poster should provide a piping diagram of the site; I think it’s caused by the flow pattern of the fluid.
Reply #72017-09-04
Let’s play a riddle game. One end of the pipe is closed. When the first pump is started, fluid flows in, so there is flow. When the second pump is started, no more fluid can flow through the system; since the fluid doesn’t move, there is no flow either

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.