An intelligent locator – a signal below 70% from the DCS is sufficient; the valve can operate normally; When the DCS sends a signal of over 70%, the valve fails to operate, and the DCS issues an alarm; the alarm message is the same as that indicated by a disconnected locator. Please help analyze what’s going on.
Reply #22017-09-13
If it is intelligent, a maximum opening of 70% may have been set.
Reply #32017-09-13
Enter the valve positioner, set the maximum opening to 100%, and disable the alarm; this should be available in the basic settings.
Reply #42017-09-13
The maximum opening should be reset to 100%.
Reply #52017-09-13
A locator with DCS alarm output? The poster, please explain this part in detail
Reply #62017-09-13
This is not a matter related to the locator, but rather to the DCS configuration. For reasons of production safety, certain control loops have limits set on the opening degree of the control valves; in other words, the control valves in these loops cannot open beyond a certain degree. Once this opening degree value is specified in the configuration settings, the output of the regulator will not exceed the current value corresponding to that degree, and as a result, the control valve will not move. An alarm will then be generated on the regulator or the DCS operation interface. It’s a problem with the DCS system settings, not with the on-site control valves. In industrial plants, it is common to set a lower output limit as a means of controlling variable-frequency pumps. To prevent these pumps from running idle without delivering any flow, they have a minimum output frequency; the corresponding control current signal is set on the DCS, so that there is no situation where the output is 4 milliamps.
Reply #72017-09-14
The circuit current can be measured first, and then it can be determined whose fault it is.
Reply #82017-09-14
Check whether the valve requires a limited opening degree. If the design requires a maximum valve opening of 70%. A setting requirement was added in DCS.
Reply #92017-09-14
There is no setpoint limit in the DCS, nor in the locator; we had thought of this long ago. I suspect it’s a load issue with the locator, but I can’t find solid evidence.
Reply #102017-09-14
When the DCS sends a signal of over 70%, the valve fails to operate, and the DCS issues an alarm; this alarm indicates that the corresponding AO channel of the DCS is open-circuited.
Reply #112017-09-15
Intelligent locator: It can resolve at least 60% of problems through self-checking and automatic stroke adjustment

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.