There is an FO control valve: the control room sets it at 25% while the field value is 75%. What could be the reason for this? How can it be configured so that the values in the control room and the field are identical? What is the function of a locator? I study engineering, so I don’t really understand the mechanics of instruments
Reply #22018-07-18
In FO mode, with air-shut operation, the valve is fully open at 4 mA (the current setpoint of 0%) and fully closed at 20 mA (the current setpoint of 100%). It is necessary for the DCS configuration personnel to change the AO output setting from air-open to air-shut, so that 20 mA is output when the setpoint is 0% and 4 mA is output when the setpoint is 100%
Reply #32018-07-18
The range of the AO output module can be changed; it was originally 4-20mA, and changing it to 20-4mA will do
Reply #42018-07-18
Please tell me which brand of DCS or PLC it is, and Haiyou can provide more specific assistance to you.
Reply #52018-07-18
Just change the reaction on the locator directly, that’s it

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.