2018-07-25View Original

Thread Content

I want to use a PID controller to regulate two valves; the CV values, minimum and maximum flow rates of these two valves are known, as is their control ratio. To achieve smoother adjustment and minimize disruption to the user, I’d like to know how to calculate this split point. I hope those with more experience can offer some help; thank you!
Reply #22018-07-25
If the characteristics of the two valves are identical (both linear or equal percentage type), and their operation mode is the same (both air-actuated open or air-actuated closed), the equivalent valve still needs to retain its original characteristics; therefore, it is necessary to select the split point correctly.
Reply #32018-07-25
There are two common methods for determining division points: the continuous division method and the interval division method.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.