Thread Content
Control an oil pump using an ABB frequency converter. How can the following process be achieved?
1. Upon receiving the start signal, the pump starts up and operates from 0 Hz to 30 Hz, after which it runs at a frequency of 30 Hz. 2. After some time, adjust the operating frequency manually to an appropriate value based on the operating conditions
I need you to provide further clarification: 1. By \"manual adjustment,\" do you mean adjusting it using a panel? Should it still be adjusted using the remote end (DCS)? 2. Where is your pump started from, an on-site start button? Still a panel? Still DCS? 3. Is the frequency of manual adjustment upward or downward, or is either possible?
Start/stop of control system? If so, the inverter has a start terminal and a 4–20mA input terminal; the two wires are connected to the system’s DO points, and the inverter starts when a start signal is sent from the system ; By setting the frequency value to 30HZ in the system settings, you can basically achieve the function you want. I just don’t know if you have any requirements regarding the frequency range of 0~30HZ
This is the most basic setting; the startup time is 30 seconds or even longer. You can set it according to your needs, and when 30 seconds have passed, the frequency will reach 30Hz; This requires a second setting: a minimum frequency of 30Hz. After completing these two settings, adjust the frequency freely after it starts up, but it must not be lower than 30Hz; thus, what you mentioned will be achieved.