When designing instruments, should the signal type be taken into consideration for the instrument circuits in an instrument junction box? For example, intrinsically safe signals and non-intrinsically safe circuits need to be separated.
Reply #22018-12-16
Intrinsic safety signals and non-intrinsic safety circuits should be separated; it is advisable to install separate wiring boxes for intrinsic safety signals and those for non-intrinsic safety circuits.
Reply #32018-12-16
Separate them. For example, those that require 220V power supply need to be separated from 4–20mA signals; three-wire heating resistors and combustible gas detectors also generally have their own wiring boxes
Reply #42018-12-16
Intrinsic safety vs. non-intrinsic safety, with a separation for those connected to SIS and those not connected to SIS, as well as a separation between 220V and 24V

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.