This post was last edited by ringdent_XWPR on 2020-6-9 at 14:44. When detecting flammable gases or toxic gases that are heavier than air, the installation height of the detector should be between 0.3m and 0.6m above the floor (or floor slab); when detecting flammable gases or toxic gases that are lighter than air, the installation height of the detector should be within 2.0m above the source of emission. When detecting flammable gases or toxic gases that are slightly heavier than air, the installation height of the detector should be between 0.5 m and 1.0 m below the source of release; when detecting flammable gases or toxic gases that are slightly lighter than air, the installation height of the detector should be between 0.5 m and 1.0 m above the source of release. 4.1.2 To determine whether the leaking gas is heavier than air, the ratio of the molecular weight of the leaking gas to that of ambient air should be used as a basis, and the following principles should apply: 1 If the ratio is greater than or equal to 1.2, then the leaking gas is heavier than air ; 2 When the ratio is greater than or equal to 1.0 and less than 1.2, the leaking gas is slightly heavier than air ; 3 When the ratio is between 0.8 and 1.0, the leaking gas is slightly lighter than air ; 4 When the ratio is less than or equal to 0.8, the leaking gas is lighter than air. Besides hydrogen, what other gases are lighter than air?
Roughly calculated, air is 29 and nitrogen is 28; based on this figure
All gases with a mass fraction of less than 29 are lighter than air
Ammonia and the like are generally lighter than air when their molecular weight is less than 29
Our facility has hydrogen, carbon monoxide, methane, acetylene, and ammonia