2020-10-20View Original

Thread Content

Why are the main shielding wires of the multi-core main cables for total screen and split-screen in the new regulations grounded both at the site and in the cabinet room? Won’t this cause signal interference?
Reply #22021-03-10
In the junction box, only the main panel is grounded; the sub-panels are connected to the field signal grounding wires that lead to the field. However, the instruments in the field are grounded through the armored layer, so the sub-panels remain single-ended grounded
Reply #32021-03-14
I’ve learned it, thanks to the original poster! ! ! ! ! ! !
Reply #42021-03-15
Standard setters are nothing. Since it is a main panel, it should not be connected to the protective ground, unless it is an armored cable. But actually, it doesn’t make much of a difference, because grounding the split screens will shield the electromagnetic field of the main screen; so as long as the individual split screens are grounded, there’s no problem.
Reply #52021-08-02
What is this standard, and where can I download it?
Reply #62021-08-02
The armor, main panel, and enclosure shall be connected to the protective ground, with both ends grounded as close as possible. The branch shield layer serves a shielding purpose; the field end is not grounded, while it is grounded on the control cabinet side, and the wiring box must not be interrupted. If there is no split screen, the main screen is connected to the ground.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.