Process Engineering Division – Instrumentation and Automation Section – Daily Topics – Topic No. 2020-12-08: Discussion question: When the detection system for 320, nickel-chromium/nickel-silicon thermocouples is in operation, the temperature at its cold end is t0 = 30°C. The instrument measures the thermoelectromotive force E(t, t0) = 39.17 mV. Determine the actual temperature of the medium being measured. (5 points are given only to those who provide the correct answer; additional points are awarded for a correct calculation process or detailed explanation.)
Reply #22020-12-08
When the detection system of the nickel-chromium/nickel-silicon thermocouple is in operation, the temperature at its cold end is t0=30°C. The instrument measures the thermoelectric potential as E(t,t0)=39.17 mV. According to the table, the thermoelectric potential at E(30,0) is 1.2 mV. Therefore, E(t,0) = E(t,30) + E(30,0), which equals 39.17 mV + 1.2 mV = 40.37 mV. Referring to the table again, a thermoelectric potential of 40.37 mV corresponds to a temperature of 977°C. The actual temperature of the medium under test is 977°C.
Reply #32020-12-08
According to the table, the thermoelectric potential E(30,0) is 1.2 mV. The thermoelectric potential E(t,0) equals E(t,30) plus E(30,0), that is, 39.17 mV + 1.2 mV = 40.37 mV. Again, per the table, a thermoelectric potential of 40.37 mV corresponds to a temperature of 977°C. The actual temperature of the medium under test is 977°C.
Reply #42020-12-08
According to the table, the thermoelectric potential E(30,0) is 1.2 mV. The thermoelectric potential E(t,0) equals E(t,30) plus E(30,0), that is, 39.17 mV + 1.2 mV = 40.37 mV. Again, per the table, a thermoelectric potential of 40.37 mV corresponds to a temperature of 977°C. The actual temperature of the medium under test is 977°C.
Reply #52020-12-08
According to the table, the thermoelectric potential E(30,0) is 1.2 mV. The thermoelectric potential E(t,0) equals E(t,30) plus E(30,0), that is, 39.17 mV + 1.2 mV = 40.37 mV. Again, per the table, a thermoelectric potential of 40.37 mV corresponds to a temperature of 977°C. The actual temperature of the medium under test is 977°C.
Reply #62020-12-08
E(t0,0)+E(t,t0)=E(t,0)
Reply #72020-12-08
The actual temperature of the medium under test is 977°C. I’ve learned it.*
Reply #82020-12-08
The cold-end temperature of the chromium-nickel-silicon thermocouple is 30°C. According to the table, the thermoelectromotive force E(30,0) is 1.2 mV. The instrument measures the thermoelectromotive force as E(t,t0) = 39.17 mV. Therefore, E(t,0) = E(t,30) + E(30,0) = 39.17 mV + 1.2 mV = 40.37 mV. According to the table, a value of 40.37 mV corresponds to a temperature of 977°C; thus, the actual temperature of the medium being measured is 977°C.
Reply #92020-12-08
According to the table, the thermoelectric potential E(30,0) is 1.2 mV. The thermoelectric potential E(t,0) equals E(t,30) plus E(30,0), that is, 39.17 mV + 1.2 mV = 40.37 mV. Again, per the table, the temperature corresponding to a thermoelectric potential of 40.37 mV is 977°C. The actual temperature of the medium under test is 977°C.
Reply #102020-12-08
According to the table, the thermoelectric potential E(30,0) is 1.2 mV. The thermoelectric potential E(t,0) equals E(t,30) plus E(30,0), that is, 39.17 mV + 1.2 mV = 40.37 mV. Again, per the table, the temperature corresponding to a thermoelectric potential of 40.37 mV is 977°C. The actual temperature of the medium under test is 977°C.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.